I'm going to post this here because doesn't seem like people posting on the Apex forum are getting answered very quickly...
Check my code on my heaters.
What I want is the heater to be off for 15 minutes when feeda is activated and also turn off for 35 minutes when feedb is activated. And of course to do the normal, on when temp hits 77.9 and off when it hits 79.1 Does this look right? And also to prevent probe issue from causing it to stick on then lower than 73 its off. Let me know if I did something silly here?
Fallback OFF
If DisTmp < 78.0 Then ON
If DisTmp > 79.0 Then OFF
If DisTmp < 73.0 Then OFF
If FeedA 015 then off
If feedB 035 then off
And my second heater's prog looks like this. Idea is similar for this heater but for if the other heater isn't able to maintain the temp or temp drops too low this is the backup. I live in a cold env and want to have a secondary heater to takeover if the first cant keep up.
Fallback OFF
If DisTmp < 76.5 Then ON
If DisTmp > 78.0 Then OFF
If DisTmp < 72.0 Then OFF
If FeedA 015 then off
If FeedB 035 then off
And then my second question...
Havent done much with the timing statements. I have a gyre and want to set a specific time every day that it is off for 15 minutes... I'm sure this is pretty simple but I'd rather not screw it up. Thanks in advance!
I'd assume it'd be something like this...
Fallback On
Set On
If time 22:00 then off
If time 22:15 then on
Or is this totally wrong?
Check my code on my heaters.
What I want is the heater to be off for 15 minutes when feeda is activated and also turn off for 35 minutes when feedb is activated. And of course to do the normal, on when temp hits 77.9 and off when it hits 79.1 Does this look right? And also to prevent probe issue from causing it to stick on then lower than 73 its off. Let me know if I did something silly here?
Fallback OFF
If DisTmp < 78.0 Then ON
If DisTmp > 79.0 Then OFF
If DisTmp < 73.0 Then OFF
If FeedA 015 then off
If feedB 035 then off
And my second heater's prog looks like this. Idea is similar for this heater but for if the other heater isn't able to maintain the temp or temp drops too low this is the backup. I live in a cold env and want to have a secondary heater to takeover if the first cant keep up.
Fallback OFF
If DisTmp < 76.5 Then ON
If DisTmp > 78.0 Then OFF
If DisTmp < 72.0 Then OFF
If FeedA 015 then off
If FeedB 035 then off
And then my second question...
Havent done much with the timing statements. I have a gyre and want to set a specific time every day that it is off for 15 minutes... I'm sure this is pretty simple but I'd rather not screw it up. Thanks in advance!
I'd assume it'd be something like this...
Fallback On
Set On
If time 22:00 then off
If time 22:15 then on
Or is this totally wrong?