New member
So installed a ATK and it seems to function fine, but it alarms every time it finishes a top up this is driving me nuts 3000 emails later
I posted this in the apex section

Installed an ATK last night to my Apex EL, and im getting constant alarms. UNit is installed with bottom optical just at water line. I have currently set my alarm email status to off. Please help. :headwally::headwally:


Item Date Status Statement
1 2018-11-22 00:21:35 -0500 ON If Swx3_1 CLOSED Then ON
2 2018-11-22 01:21:34 -0500 ON If Swx3_1 CLOSED Then ON
3 2018-11-22 02:21:35 -0500 ON If Swx3_1 CLOSED Then ON
4 2018-11-22 03:21:36 -0500 ON If Swx3_1 CLOSED Then ON
5 2018-11-22 04:03:50 -0500 OFF Set OFF
6 2018-11-22 04:03:53 -0500 ON If Swx3_1 CLOSED Then ON
7 2018-11-22 04:10:23 -0500 ON Set OFF
8 2018-11-22 04:10:25 -0500 ON If Swx3_1 CLOSED Then ON
9 2018-11-22 04:11:07 -0500 OFF Set OFF
10 2018-11-22 04:11:45 -0500 ON If Swx3_1 CLOSED Then ON
 
It looks like you might have added the lower optical sensor to the email alarm outlet. When you run the ATK task programming it ONLY puts the upper optical sensor and the Error ATK alarm not the lower optical sensor. The reason we do not add that is because the water covers and uncovers the lower sensor all the time and it will give alarms like you are having.

I would remove that line of programming from the email alarm and why you are at it add this to the end of the email outlet.

Defer 000:30 Then ON
 