I have a quick question for you ACIII programming experts. I would like the unit to send me a daily email to my Blackberry, so when I'm travelling, I can just get a quick check of tank parameters without having to log in to the system via the Internet. Assuming I have the unit set up to send me email alarms, I'm thinking something along the following lines might work. I have no audible alarms hooked up (so I don't have to worry about the beeping while the alarm is active), because I always have my Blackberry on me to receive immediate alarms by email, and because I do not use any X10.
If Time > 00:00 Then ALM OFF
If Time > 14:00 Then ALM ON
If Time > 14:05 Then ALM OFF
Anyone know if this will work to send me a tank status update at 2:00 PM every day? Are there any other ways of doing it?
Also, here's what I'm planning on using for a program. As you can see, I do use the seasonal temperature tables, but not the seasonal sunrise/sunset or moonlight tables. Anyone see any problems or have any suggestions?
MH1$-D14 (1st pair of MHs)
MH2$-D15 (2nd pair of MHs)
MH3$-D16 (3rd pair of MHs)
PC1$-C8 (1st set of PCs)
PC2$-C6 (2nd set of PCs)
REF$-D13 (refugium light)
FAN%-A4 (cooling fans)
KAL#-A1 (kalk reactor stirrer)
CH1%-D4 (chiller 1)
CH2%-B12 (chiller 2)
HET%-D3 (heater)
SKM#-B10 (skimmer)
OZN&-B9 (ozone generators)
H2O&-B11 (water feed through kalk reactor)
CO2&-A2 (CO2 for calcium reactor)
ALM&-J13 (alarm - no audible alarm hooked up)
MON$-C7 (moonlights)
PM1#-D1 (refugium powerhead 1)
PM2#-D2 (refugium powerhead 2)
If Time > 00:00 Then SKM ON
If Time > 00:00 Then OZN ON
If Time > 00:00 Then ALM OFF
If Time > 14:00 Then ALM ON
If Time > 14:05 Then ALM OFF
If Time > 14:00 Then REF OFF
If Time > 23:00 Then REF ON
If Time > 08:00 Then MON OFF
If Time > 23:30 Then MON ON
If Time > 13:40 Then PC1 ON
If Time > 23:40 Then PC1 OFF
If Time > 13:50 Then PC2 ON
If Time > 23:50 Then PC2 OFF
If Time > 14:00 Then MH1 ON
If Time > 23:00 Then MH1 OFF
If Time > 14:15 Then MH2 ON
If Time > 23:15 Then MH2 OFF
If Time > 14:30 Then MH3 ON
If Time > 23:30 Then MH3 OFF
If Temp < 65.0 Then MH1 OFF
If Temp < 65.0 Then MH2 OFF
If Temp < 65.0 Then MH3 OFF
If Temp > RT+0.5 Then MH1 OFF
Max Change 030 M Then MH1 OFF
If Temp > RT+0.7 Then MH3 OFF
Max Change 030 M Then MH3 OFF
If Temp > RT+0.9 Then MH2 OFF
Max Change 030 M Then MH2 OFF
If Temp > RT+0.9 Then REF OFF
Max Change 030 M Then REF OFF
If Temp < RT+-0.3 Then HET ON
If Temp < 65.0 Then HET OFF
If Temp > RT+0.0 Then HET OFF
Max Change 010 M Then HET OFF
If Temp > RT+0.1 Then FAN ON
If Temp < RT+-0.1 Then FAN OFF
Max Change 010 M Then FAN OFF
If Temp > RT+0.3 Then CH1 ON
If Temp < RT+0.0 Then CH1 OFF
Max Change 015 M Then CH1 OFF
If Temp > RT+0.3 Then CH2 ON
If Temp < RT+0.0 Then CH2 OFF
Max Change 015 M Then CH2 OFF
If pH > 7.92 Then CO2 ON
If pH < 7.90 Then CO2 OFF
Max Change 010 M Then CO2 ON
If ORP < 380 Then OZN ON
If ORP > 400 Then OZN OFF
Max Change 010 M Then OZN ON
If Time > 00:00 Then H2O ON
If Time > 00:30 Then H2O OFF
If Time > 04:00 Then H2O ON
If Time > 04:35 Then H2O OFF
If Time > 08:00 Then H2O ON
If Time > 08:35 Then H2O OFF
If Time > 12:00 Then H2O ON
If Time > 12:30 Then H2O OFF
If Time > 16:00 Then H2O ON
If Time > 16:25 Then H2O OFF
If Time > 20:00 Then H2O ON
If Time > 20:25 Then H2O OFF
If pH > 8.50 Then H2O OFF
If Time > 03:30 Then KAL ON
If Time > 03:40 Then KAL OFF
If Time > 07:30 Then KAL ON
If Time > 07:40 Then KAL OFF
If Time > 11:30 Then KAL ON
If Time > 11:40 Then KAL OFF
If Time > 15:30 Then KAL ON
If Time > 15:40 Then KAL OFF
If Time > 19:30 Then KAL ON
If Time > 19:40 Then KAL OFF
If Time > 23:30 Then KAL ON
If Time > 23:40 Then KAL OFF
OSC 030/030 ON/OFF Then PM1 ON
OSC 030/030 ON/OFF Then PM2 OFF
If Feed cycle Then SKM OFF
If Timer SKM = OFF Then OZN OFF
If Temp > RT+0.7 Then ALM ON
If Temp < RT+-0.7 Then ALM ON
If pH > 8.50 Then ALM ON
If pH < 7.85 Then ALM ON
If ORP > 420 Then ALM ON
If ORP < 350 Then ALM ON
If Power Fail Then ALM ON
Please let me know if you have any suggestions.
Thanks.
-Todd
If Time > 00:00 Then ALM OFF
If Time > 14:00 Then ALM ON
If Time > 14:05 Then ALM OFF
Anyone know if this will work to send me a tank status update at 2:00 PM every day? Are there any other ways of doing it?
Also, here's what I'm planning on using for a program. As you can see, I do use the seasonal temperature tables, but not the seasonal sunrise/sunset or moonlight tables. Anyone see any problems or have any suggestions?
MH1$-D14 (1st pair of MHs)
MH2$-D15 (2nd pair of MHs)
MH3$-D16 (3rd pair of MHs)
PC1$-C8 (1st set of PCs)
PC2$-C6 (2nd set of PCs)
REF$-D13 (refugium light)
FAN%-A4 (cooling fans)
KAL#-A1 (kalk reactor stirrer)
CH1%-D4 (chiller 1)
CH2%-B12 (chiller 2)
HET%-D3 (heater)
SKM#-B10 (skimmer)
OZN&-B9 (ozone generators)
H2O&-B11 (water feed through kalk reactor)
CO2&-A2 (CO2 for calcium reactor)
ALM&-J13 (alarm - no audible alarm hooked up)
MON$-C7 (moonlights)
PM1#-D1 (refugium powerhead 1)
PM2#-D2 (refugium powerhead 2)
If Time > 00:00 Then SKM ON
If Time > 00:00 Then OZN ON
If Time > 00:00 Then ALM OFF
If Time > 14:00 Then ALM ON
If Time > 14:05 Then ALM OFF
If Time > 14:00 Then REF OFF
If Time > 23:00 Then REF ON
If Time > 08:00 Then MON OFF
If Time > 23:30 Then MON ON
If Time > 13:40 Then PC1 ON
If Time > 23:40 Then PC1 OFF
If Time > 13:50 Then PC2 ON
If Time > 23:50 Then PC2 OFF
If Time > 14:00 Then MH1 ON
If Time > 23:00 Then MH1 OFF
If Time > 14:15 Then MH2 ON
If Time > 23:15 Then MH2 OFF
If Time > 14:30 Then MH3 ON
If Time > 23:30 Then MH3 OFF
If Temp < 65.0 Then MH1 OFF
If Temp < 65.0 Then MH2 OFF
If Temp < 65.0 Then MH3 OFF
If Temp > RT+0.5 Then MH1 OFF
Max Change 030 M Then MH1 OFF
If Temp > RT+0.7 Then MH3 OFF
Max Change 030 M Then MH3 OFF
If Temp > RT+0.9 Then MH2 OFF
Max Change 030 M Then MH2 OFF
If Temp > RT+0.9 Then REF OFF
Max Change 030 M Then REF OFF
If Temp < RT+-0.3 Then HET ON
If Temp < 65.0 Then HET OFF
If Temp > RT+0.0 Then HET OFF
Max Change 010 M Then HET OFF
If Temp > RT+0.1 Then FAN ON
If Temp < RT+-0.1 Then FAN OFF
Max Change 010 M Then FAN OFF
If Temp > RT+0.3 Then CH1 ON
If Temp < RT+0.0 Then CH1 OFF
Max Change 015 M Then CH1 OFF
If Temp > RT+0.3 Then CH2 ON
If Temp < RT+0.0 Then CH2 OFF
Max Change 015 M Then CH2 OFF
If pH > 7.92 Then CO2 ON
If pH < 7.90 Then CO2 OFF
Max Change 010 M Then CO2 ON
If ORP < 380 Then OZN ON
If ORP > 400 Then OZN OFF
Max Change 010 M Then OZN ON
If Time > 00:00 Then H2O ON
If Time > 00:30 Then H2O OFF
If Time > 04:00 Then H2O ON
If Time > 04:35 Then H2O OFF
If Time > 08:00 Then H2O ON
If Time > 08:35 Then H2O OFF
If Time > 12:00 Then H2O ON
If Time > 12:30 Then H2O OFF
If Time > 16:00 Then H2O ON
If Time > 16:25 Then H2O OFF
If Time > 20:00 Then H2O ON
If Time > 20:25 Then H2O OFF
If pH > 8.50 Then H2O OFF
If Time > 03:30 Then KAL ON
If Time > 03:40 Then KAL OFF
If Time > 07:30 Then KAL ON
If Time > 07:40 Then KAL OFF
If Time > 11:30 Then KAL ON
If Time > 11:40 Then KAL OFF
If Time > 15:30 Then KAL ON
If Time > 15:40 Then KAL OFF
If Time > 19:30 Then KAL ON
If Time > 19:40 Then KAL OFF
If Time > 23:30 Then KAL ON
If Time > 23:40 Then KAL OFF
OSC 030/030 ON/OFF Then PM1 ON
OSC 030/030 ON/OFF Then PM2 OFF
If Feed cycle Then SKM OFF
If Timer SKM = OFF Then OZN OFF
If Temp > RT+0.7 Then ALM ON
If Temp < RT+-0.7 Then ALM ON
If pH > 8.50 Then ALM ON
If pH < 7.85 Then ALM ON
If ORP > 420 Then ALM ON
If ORP < 350 Then ALM ON
If Power Fail Then ALM ON
Please let me know if you have any suggestions.
Thanks.
-Todd