Help me configure PIII

michaelangello

New member
Hi I got myself a profilux 3 and a few gadgets to go with it. What ive been trying to do is set it up properly!

I have my 3 pump doser connected to the s1-s4 and I also have my PAB power bar connected to the PAB Port.

I know then the s1-s4 are reserved when trying to configure my pab bar but if i set s5 to turn on the 5th socket on my power bar turns on and if i set s1 to always on this turns on pump1 on the dosing unit and socket 1 on the PAB bar.

What am i doing wrong?

Thanks in advance!:fun2:
 
You need to configure the power bar to start on S5. As is right now, you have both the S1-S4 on the powerbar and the doser unit tied together.
To configure the powerbar, you must go to configure, PAB, and select the 1st starting socket on the powerbar to be socket 5 in the PIII controller.
This can only be done in the controller and not the software.
 