BeanAnimal
Premium Member
You have to also understand what a UPS is really for...
We size UPS systems to hold a system up during a power outage LONG ENOUGH FOR THE GENSET TO KICK IN.
There are two ratings to consider. The CURRENT that the UPS can handle and the SIZE of the battery string.
SO when you see 500VA 750VA 1000VA etc, you are not just looking at battery size. The larger capacity units usually have larger batteries but that is only to keep up with the current draw.
It gets VERY expensive to add battery strings to ANY UPS system. It is almost always MUCH cheaper to only add enough cells to hold the system over for the genset (usually much less than 30 seconds).
I have a some VERY LARGE ups systems here, 1 with over 28 12.5Ah batteries. It will cost $400 every 3 years to replace those cells. The other UPS holds larger AGM batteries and costs around $800 when battery replacement comes around. I would be silly to put that thing on my aquarium. I can get a natural gas generator and automatic transfer switch for less than $2000.
We size UPS systems to hold a system up during a power outage LONG ENOUGH FOR THE GENSET TO KICK IN.
There are two ratings to consider. The CURRENT that the UPS can handle and the SIZE of the battery string.
SO when you see 500VA 750VA 1000VA etc, you are not just looking at battery size. The larger capacity units usually have larger batteries but that is only to keep up with the current draw.
It gets VERY expensive to add battery strings to ANY UPS system. It is almost always MUCH cheaper to only add enough cells to hold the system over for the genset (usually much less than 30 seconds).
I have a some VERY LARGE ups systems here, 1 with over 28 12.5Ah batteries. It will cost $400 every 3 years to replace those cells. The other UPS holds larger AGM batteries and costs around $800 when battery replacement comes around. I would be silly to put that thing on my aquarium. I can get a natural gas generator and automatic transfer switch for less than $2000.