This is for my new-to-me swimming pool pumphouse, but I believe addresses a few points applicable to folks running a new subpanel for their reefs. Just replace the word pool with tank everytime you see it below. It works. I swear.
I am replacing the simple on/off switch for the pool pump with a timer, and had to open the subpanel to run a neutral and ground out to the adjacent timer since the old switch was just a light switch wired into the hot for the pump circuit.
I discovered that the subpanel was wired with ground and neutral on a common bus, which, after consulting the internet, I discovered is not appropriate for a subpanel. The subpanel feeds several other devices/lights/etc already wired in inappropriately.
The problem is that the main feed only has the two hots and a neutral, no ground. It enters the pool pumphouse housed in a metallic pipe with metal fittings and comes underground from the house.
If I establish electrical continuity between the subpanel housing and the pipe as it enters the ground, can I just put in a new bus, screw it into the housing, and wire into it all of the ground wires currently on the neutral bus ? i.e. does the ground bus on the sub panel have to be in continuity with the ground wires of the main panel?
Thanks. Goooooooo reefs!!!
I am replacing the simple on/off switch for the pool pump with a timer, and had to open the subpanel to run a neutral and ground out to the adjacent timer since the old switch was just a light switch wired into the hot for the pump circuit.
I discovered that the subpanel was wired with ground and neutral on a common bus, which, after consulting the internet, I discovered is not appropriate for a subpanel. The subpanel feeds several other devices/lights/etc already wired in inappropriately.
The problem is that the main feed only has the two hots and a neutral, no ground. It enters the pool pumphouse housed in a metallic pipe with metal fittings and comes underground from the house.
If I establish electrical continuity between the subpanel housing and the pipe as it enters the ground, can I just put in a new bus, screw it into the housing, and wire into it all of the ground wires currently on the neutral bus ? i.e. does the ground bus on the sub panel have to be in continuity with the ground wires of the main panel?
Thanks. Goooooooo reefs!!!