geothermal chiller

<a href=showthread.php?s=&postid=7749989#post7749989 target=_blank>Originally posted</a> by looser

Works like a charm. The input temp is 57 degrees (ground water temp from my well), and the output to the drain is about 73 degrees. I set the flow to about 30GPH but it doesn't run for more than 10 or 15 mins before the temp drops to 80 and the valve shuts off the water supply.

WELL DONE LAD! I am excited to hear this news, kudos and thanks for sharing the results.
 
Cudy2K - Thanks! My pleasure.

I will be sure to update everyone after I figure out the actual water usage. In fact I will run the drain into a barrel right now and see what it uses today. Hopefully I'll be able to get some pictures posted sometime later today as well.
 
Looser,
Great news! My original concern was that it would take a lot of water to cool your system, thus raising the cost of the power bill, and more wear and tear on your well pump. Glad to hear that it works with such little flow:)
 
H20ENG - Thanks. Its not as much water as I thought either, although I have yet to really determine what it takes (see below). Although I do know for sure that 30GPH is more than enough to keep up with the heat load. In fact I might slow it down a little to try and exchange even more heat from the tank per gallon of cooling water (raise the output temp). I could also add some more hose and/or another length of titanium to increase the exposure/dwell time.

One little problem with my drain in a barrel plan. The drain in my tank room floor, which goes to a barrel in my basement, had a bottle cap fall into it at some point. It made a perfectly water tight seal in my drain. Needless to say the drain backed up into my tank room and flooded it and my basement. So. . . . . estimatimating water usage based on what I sucked up with my wet dry vac, about 30 gallons, I'm guessing I would use somplace between 60 and 100 gallons on average summer day to cool my tank.

With that said.... I relize my wet dry vac theory is probably not very scientific...so I guess I'll have to start my little experiment over again now that I removed the bottle cap.

Fun. . . Fun. . . Fun. . .
 
Just put hash marks on your basement wall, and then do the math when it gets to the first floor :D
 
<a href=showthread.php?s=&postid=7753450#post7753450 target=_blank>Originally posted</a> by H20ENG
Just put hash marks on your basement wall, and then do the math when it gets to the first floor :D

Of course this thread will get moved to the large tanks forum:eek1: :lol:
 
Just checked my barrel. glad I did. Its about 4" from the top. So lets say 50 gallons since 3pm. So its averaging just under 10GPH with lights on. I guess thats more than I should be dumping in my septic system for no reason at all. . . . so fortunately (I guess) I have a sump pump in my basement that drains out to the street. I'll have to tie my heat exchanger drain into the dischare pipe of the sump pump. Or maybe theres a better use of the water. . .. hmmm.... on the other hand, if it only requires 10GPH to cool the tank I could slow down the flow to lets say 15GPH and extract more heat, therfore required even less water.

Heck if I slow it down enough maybe it will even start making water..... you guys are the ones that go me started. :-)
 
On second thought. I might be better off adding more pipe rather than slow down the flow. I probably could slow the flow somewhat, but then less of the pipe would be as cold as it is now so it wouldn't be a linear relationship between GPH and heat exchange. But if I added more pipe, the existing pipe would remain the same temp as now, but I would get additional heat transfer from the additional pipe. Maybe I’d get another 5 degrees out of the cooling water. That would cut my water usage by about a third. I guess that’s worth the extra $100 for another 5’ of titanium pipe. Fortunately my sump is big enough so now that I have the system set up, adding pipe will be easy.
 
<a href=showthread.php?s=&postid=7753047#post7753047 target=_blank>Originally posted</a> by looser


One little problem with my drain in a barrel plan. The drain in my tank room floor, which goes to a barrel in my basement, had a bottle cap fall into it at some point. It made a perfectly water tight seal in my drain. Needless to say the drain backed up into my tank room and flooded it and my basement. So. . . . . estimatimating water usage based on what I sucked up with my wet dry vac, about 30 gallons, I'm guessing I would use somplace between 60 and 100 gallons on average summer day to cool my tank.

Ouch! Bummer, Stuff happens, sorry to hear that.

When you get that cleaned up could you do us a favor and measure the entering AND the leaving water temps? Knowing that and the flow volume we can calculate the BTUH removed.
 
Cudy2k - I just re-measured a little more precisely this time. Input temp is 56. Output is 72. GPH is 26.7 I’m curious to see what you come up with. Thanks.
 
<a href=showthread.php?s=&postid=7764677#post7764677 target=_blank>Originally posted</a> by looser
Cudy2k - I just re-measured a little more precisely this time. Input temp is 56. Output is 72. GPH is 26.7 I’m curious to see what you come up with. Thanks.

Cool info.

Roughly; BTUH = Delta T * GPM * 500.

So BTUH = 3560

Not to shabby!
 
Looser, do you use the well water for drinking, etc in the house or is it just for watering the yard and such. If the later, would it be possible to just pump the warm water right back down the well or some other area where it can filter back down in the ground so you are not totally wasting it?
 
<a href=showthread.php?s=&postid=7770124#post7770124 target=_blank>Originally posted</a> by chicken
Looser, do you use the well water for drinking, etc in the house or is it just for watering the yard and such. If the later, would it be possible to just pump the warm water right back down the well or some other area where it can filter back down in the ground so you are not totally wasting it?

Chicken - We use the well water for all the house needs. Right now the water goes into my septic system which leaches back into the ground, but I'm going to change that so that it goes into my sump pump in the basement which eventualy makes it to a river and back to the ocean.

I really don't concider it wasting water though. There is so much water in my area that my yard is still mud from the spring, and I need a sump pump in my basement so it doesn't flood when it rains. The water doesn't get polluted and it stays right here in the good old earth. What does get "wasted" is the electricity it takes to pump the water from well, so thats why I'd like to minimize the water usage. Although I'm pretty certain its still less electricty than it would take to run a chiller.
 
<a href=showthread.php?s=&postid=7768302#post7768302 target=_blank>Originally posted</a> by Cuby2k
Cool info.

Roughly; BTUH = Delta T * GPM * 500.

So BTUH = 3560

Not to shabby!

Cuby2 - Thanks, but I'm afraid I don't have a reference for the number. What does that equate to in laymen terms? Also, any idea what the equivalent cost would be if I where to use a chiller for the equivalent cooling? I could probably figure out what it costs me to run my well pump to pump an hours worth of water. Just trying to take it the next step and try and figure out what the actual savings are beyond the initial cost of the chiller of course.
 
<a href=showthread.php?s=&postid=7770641#post7770641 target=_blank>Originally posted</a> by BeanAnimal
and evaporating 1 gallon of water gives you over 7000 BTU of cooling :)


Now thats interesting. Sounds like installing another fan might help cut down on water usage a lot.
 
<a href=showthread.php?s=&postid=7770594#post7770594 target=_blank>Originally posted</a> by looser
Cuby2 - Thanks, but I'm afraid I don't have a reference for the number. What does that equate to in laymen terms? Also, any idea what the equivalent cost would be if I where to use a chiller for the equivalent cooling? I could probably figure out what it costs me to run my well pump to pump an hours worth of water. Just trying to take it the next step and try and figure out what the actual savings are beyond the initial cost of the chiller of course.

Looser, one ton of cooling is 12,000 BTUH. Chiller manufacturers are notorious for NOT listing cooling capacity, instead they list HP. From what I understand they equate 1 HP to 1 ton of cooling although that doesn't work out in my book. We used to figure 1 KW/ton when we'd estimate power consumption for a rooftop unit or an air cooled chiller system. That breaks out to about 1.3 HP/ton, so from that you could assume you are getting about a 0.4 HP chiller capacity. And actually you are removing heat from 1000 watts of lighting.

Bean I think that evaporation is a GREAT to go for cooling your tank with one exception. When you evaporate the heat into your home and are using a central AC system you still have to pay to remove that heat, both latent and sensible. I know evaporation is popular but it isn't free.

I think using a small cooling tower like Deltec's Eco Cooler is a nice way to go if you place the unit outdoors but again they charge an arm and a leg for that little puppy. Then there is the issue of bugs, dust and ambient temp that you have to deal with.

The entire cooling issue is like drugs, they all have side effects so none of them are perfect. Of course a cold Corona on a warm evening, sitting on the patio with your favorite mermaid and friends is pretty close . . . .ah. But then that belongs in a different thread.:rollface:
 
<a href=showthread.php?s=&postid=7771523#post7771523 target=_blank>Originally posted</a> by Cuby2k
Looser, one ton of cooling is 12,000 BTUH. Chiller manufacturers are notorious for NOT listing cooling capacity, instead they list HP. From what I understand they equate 1 HP to 1 ton of cooling although that doesn't work out in my book. We used to figure 1 KW/ton when we'd estimate power consumption for a rooftop unit or an air cooled chiller system. That breaks out to about 1.3 HP/ton, so from that you could assume you are getting about a 0.4 HP chiller capacity. And actually you are removing heat from 1000 watts of lighting.

Bean I think that evaporation is a GREAT to go for cooling your tank with one exception. When you evaporate the heat into your home and are using a central AC system you still have to pay to remove that heat, both latent and sensible. I know evaporation is popular but it isn't free.

I think using a small cooling tower like Deltec's Eco Cooler is a nice way to go if you place the unit outdoors but again they charge an arm and a leg for that little puppy. Then there is the issue of bugs, dust and ambient temp that you have to deal with.

The entire cooling issue is like drugs, they all have side effects so none of them are perfect. Of course a cold Corona on a warm evening, sitting on the patio with your favorite mermaid and friends is pretty close . . . .ah. But then that belongs in a different thread.:rollface:

Cuby2 - Thanks! I think I get it now. In fact the alternative that I had concidered was a .5 HP chiller. A .5 HP chiller cost about $1,100 or $2,200 per ton. So at .4HP I'm getting about $880 worth of cooling capacity for a cost of about $250. So, to your point, not to shabby at all :) . I wonder if I add another 25' of plastic tubing (cost about $5) if I would get another 1/10th of a HP worth of cooling?

Now for operating costs. Any thoughts on how to calculate costs to run a 1/2 HP chiller? My well pump is a 1hp pump, I think its 6amp. Could probably pump 30 gallons (or 1hrs worth of water) in about 5 minutes. (just a guess)
 