Not true. It will require a ground wire connected to it to complete the circuit properly.You most certainly can put a GFCI in place of the two-wire outlet, however any three-prong cords will not be grounded and the outlets should be labelled as such. The GF protection will still be active even without a ground connection.
It is working, that's great! But I would take it back off and ground it to the steel receptacle box (take a copper wire and attach the green lead on the receptacle to the screw on the back of the box) that will ensure a proper full ground and a fully functional GFCI.Ok I installed and tested it. Works. However, no sticker came with it so I can put no equipment ground. This is what I put on outlet correct? The outlet is safer now that I have this installed correct? I noticed also that my bathroom gfci is installed wrong bathroom light goes off as well.
True. Re-running the line is the proper full way to do it, but grounding it to the box will work and quite well.you dont have a ground at all in the box? it should be the exposed cable in the wiring. did the old outlet have a ground plug on the outlet or did it just have the 2 prongs? If it has a steel receptacle box you should ground it to that like thisguy12 said.
you really should have an electrician run a line with a ground so its properly grounded and doesn't cause a major issue.
Ok I installed and tested it. Works. However, no sticker came with it so I can put no equipment ground. This is what I put on outlet correct? The outlet is safer now that I have this installed correct? I noticed also that my bathroom gfci is installed wrong bathroom light goes off as well.
Garage not necessary but helpful. Kitchen should be gfci but again depends how close to a water source it is (+/- 3'-0").Yes I have no GFCI either on the outside outlets or my kitchen.. Time to replace all these to be safe. I heard also the garage as well that true?
Not true. It will require a ground wire connected to it to complete the circuit properly.
- Replacing Ungrounded 2-Prong Outlets with a Standard 3-Prong Outlet
- You may not replace a two prong ungrounded outlet with a standard 3-wire grounded outlet that has a ground prong unless there is a ground wire connection available.
- Installing a standard 3-wire outlet that is not grounded is not safe and is illegal by electrical code standards and this is not an acceptable practice.
- The danger is that there is no ground wire available, therefore there is no provision to interrupt the circuit in the event of a ground fault.
- Ungrounded outlets may increase the risk of electrical shock potential.
You sir are incorrect.You are NOT correct and clearly do not understand how a GFI works...per Leviton (manufacturer) Technical http://communities.leviton.com/thread/1080
here's another reference... http://ask-the-electrician.com/replacing-ungrounded-outlets-with-a-gfi/
and another... NEC Sec. 210-7(d)(3) permits any of the following installations when replacing a 2-wire ungrounded receptacle:
(a) Replace it with another 2-wire receptacle;
(b) Replace it with a GFCI-type receptacle and mark the receptacle with the words “No Equipment Ground;” or
(c) Replace it with a grounding-type receptacle protected by a GFCI device (circuit breaker or receptacle). Since the grounding terminals for the receptacles are not grounded, you must mark the receptacles with the words “GFCI Protected” and “No Equipment Ground”