There was something in the Aquactinics forums explaining why 2 ballasts turning on at the same time can trip a GFI:
Ray,
There is nothing wrong with your fixture. The problem is with the GFI (note: the GFI is working exactly the way it should be). The Constellation uses multiple ballasts within the fixture. Lighting ballast (all makes and models) have what's called leakage current. The GFI is sensitive enough to detect this "leakage current" and trips. Now typically one ballast on a GFI does not have enough "leakage current" (btw, we are talking within the milliamps "mA") to trip, but when you add more ballast the current goes up usually tripping the circuit. There are a few GFIs out there that have a higher threshold for "leakage current", namely GE and Levion(sp?). The simple solution is to use this fixture on standard outlets as the GFIs were never designed to handle lighting systems.
Thank you,
Tom
Aquactinics