Attached is a drawing of what I have. What I have found is the guy who ran the sub panel used BX with a bonding strip rather than MC with an independent ground. However the two panels are bonded together and ohm out with no problem. However if I lose a neutral on my sub panel this bonding is not going to handle and significant current so I need to fix this. I dont know if NEC allows for me to bond my sub independent to ground. The water main is 10' away and I can also sink independent grounds into the earth just outside the wall. I believe NEC will allow for that but I don't know. Either way they are currently bonded and is not the source of the 5 volts I have with nothing plugged in as I have discovered that...
I have three outlets running to my DT. Two are on a 3KVUPS and one is not. I needed the one not on a UPS because my apex needs to monitor the power so it knows when it is out and adjust the loads so the UPS lasts as long as possible. All three outlets test fine with a outlet tester. All three ohm out to ground with each other and with one outlet I have near by that runs off the main.
However when trouble shooting I noticed that if I disconnect one of the outlets from my UPS (located in the basement near my sub panel) and plug it into a GFI next to my frag system near the sub panel it pops the GFI. It will not let me reset it. However if I plug them both into the GFi, I do not pop it. It does not matter which one I plug into the UPS and which one I plug into the GFI. In either case the GFI trips. So while testing voltage in the DT If I plug outlet #1 into either the UPS or the GFI I get 0.0XXX volts in the DT. When I plug in outlet #2 in I get 3-5 volts (goes up and down). Even with nothing plugged into outlet # 2. Keep in ming both outlet 1+2 plug into a UPS in the basement and run upstairs to two outlets behind my DT. So if I have my apex plugged into outlet#1 and nothing plugged into outlet#2 I get 3-5v in my DT water. This was not the case when this was installed 4 years ago and has not been the case up until a month or so ago.
So That feed running from my UPS to my DT is causing the voltage with nothing in the water. Don't know how but don't care. It is an issue so I have abandoned that outlet as it can not be fixed with out draining and removing the DT.
So continuing on with my stray voltage trouble shooting starting at 0.0xx or lower voltage...
here is what each item adds to my voltage and the original point of my original questions.
Still with nothing contacting the water turned on. Heaters, skimmer, return pumps all off...and un-plugged. Now I know most aquarium stray voltage are inductive so I get the MP10's But DC drivers where the transformers are mounted 20" away is throwing me for a loop and the 5 volts from a 12 power supply that is over a foot away is confusing as hell...
I do have a bad skimmer pump. That is putting 16 volts into the water. I have ordered a new one...And all the other strange ancillary voltages (heaters, and return pump) are no longer an issue with just the one feed removed from the equation.
I have three outlets running to my DT. Two are on a 3KVUPS and one is not. I needed the one not on a UPS because my apex needs to monitor the power so it knows when it is out and adjust the loads so the UPS lasts as long as possible. All three outlets test fine with a outlet tester. All three ohm out to ground with each other and with one outlet I have near by that runs off the main.
However when trouble shooting I noticed that if I disconnect one of the outlets from my UPS (located in the basement near my sub panel) and plug it into a GFI next to my frag system near the sub panel it pops the GFI. It will not let me reset it. However if I plug them both into the GFi, I do not pop it. It does not matter which one I plug into the UPS and which one I plug into the GFI. In either case the GFI trips. So while testing voltage in the DT If I plug outlet #1 into either the UPS or the GFI I get 0.0XXX volts in the DT. When I plug in outlet #2 in I get 3-5 volts (goes up and down). Even with nothing plugged into outlet # 2. Keep in ming both outlet 1+2 plug into a UPS in the basement and run upstairs to two outlets behind my DT. So if I have my apex plugged into outlet#1 and nothing plugged into outlet#2 I get 3-5v in my DT water. This was not the case when this was installed 4 years ago and has not been the case up until a month or so ago.
So That feed running from my UPS to my DT is causing the voltage with nothing in the water. Don't know how but don't care. It is an issue so I have abandoned that outlet as it can not be fixed with out draining and removing the DT.
So continuing on with my stray voltage trouble shooting starting at 0.0xx or lower voltage...
here is what each item adds to my voltage and the original point of my original questions.
- MP10's .6-3 volts (varies as pumps surge)
- Apex 12v power supply 5 volts
- DIY LED Drivers 0 volts when on but ar zero percent. 1-2 volts whan ramped up to 100%
Still with nothing contacting the water turned on. Heaters, skimmer, return pumps all off...and un-plugged. Now I know most aquarium stray voltage are inductive so I get the MP10's But DC drivers where the transformers are mounted 20" away is throwing me for a loop and the 5 volts from a 12 power supply that is over a foot away is confusing as hell...
I do have a bad skimmer pump. That is putting 16 volts into the water. I have ordered a new one...And all the other strange ancillary voltages (heaters, and return pump) are no longer an issue with just the one feed removed from the equation.