WTB: Apex EB8

Can you copy and paste your program for the sticking outlets? Just curious. Please include the names as long as they are clear as to what you are controlling. Skimmer, pump, lights .....
 
Also save your configuration before swapping out modules. I learned the hard way. Wiped out all my programming on one of my eb8's. The new one grabbed the same address as the original. The conflict made my eb8 default. Luckily I had a somewhat recent back up.
 
Fallback OFF
Set OFF
If Time 18:00 to 23:30 Then ON
If Temp > 81.0 Then OFF
Min Time 000:30 Then OFF

I've used this code for 12 months with no issues on the LED light. It started sticking on outlet 5, so I cut and pasted it to outlet 3....same issue. I put it on outlet 7 and it turned off last night. Just seems like I'm asking for trouble.
 
Is this a very low watt led ? 5 or 6 watts is too low for the triacs to shut off. They don't recognize such a low load. You have to use the switched load outlets. The setup is listed in the comprehensive manual.
 