smmiller506
New member
My $0.02 - the inverter that you originally posted would work for a little while as it is an inverter and charger in one unit. I've been looking at that exact same unit as we don't have many power outages, but we did have one for 6 hours or so in town (transformer went out). The newer standby generators have a weekly auto-test and require an oil change about once every two years. If it is not a whole house generator (like the one linked to earlier), then you get a second panel, which connects to the first through a supplied two-pole circuit breaker. When the power is normally on, service entrance power flows through the main breaker, the 50 amp two-pole breaker, through the normally ON contacts of the automatic transfer switch, and finally to the aux breakers that your very important equipment is.connected to (HVAC, fridge, fish tank, etc). In the event of a power outage, the transfer switch has a sensor that reads power has been lost from the 50 amp two-pole breaker, and kicks the generator on, which then supplies power through the normally off contacta of the transfer switch. Power cannot go from the service or the generator to each other, and the aux breakers are fed from only one source at a time. A small UPS good for 10 minutes max would still be a good investment at this point as the generator takes about 10-30 seconds to supply power after the service has lost it. A UPS would bridge this gap so that there are no true interruptions in power.