Thanks for the heads up Nikon187. I have few decisions regarding plumbing which will need to be made. Once finalized we’ll size the overflow accordingly, however, I would like to keep it as small as possible without compromising function.....more on this to come.
Just like I want to do. So I will be watching.
You want the electrical hole at least 1.5" My 1.5" electrical bulkhead is practically at capacity. Its amazing how many wires go in there. You will also want two 1.5" drains. Never put a large system with one drain. Its just asking for trouble. So basically you will need to plan for 4 holes which will be about 20" x 5" or so.. Maybe you can go 10" x 10"
edit.. didn't see you changed your mind a few posts downLOL
Mike
What if you put a heavy cross-brace perpendicular to the floor joists and supported that on either side of the doorway to the cold cellar? You would have to really beef the brace up, either LVL or several 2x10s glued, screwed and tattooed together. A second supported brace running closer to the wall wouldn't go amiss, either.
Dave.M
Bioload, congrats on a great pre-plan idea, one suggestion, if you see how the Vortechs work the type of flow they produce is not straight but more like turbulent, here is a quick video,
<object width="560" height="345"><param name="movie" value="http://www.youtube.com/v/HLkW1-6HbQk?version=3&hl=en_US"></param><param name="allowFullScreen" value="true"></param><param name="allowscriptaccess" value="always"></param><embed src="http://www.youtube.com/v/HLkW1-6HbQk?version=3&hl=en_US" type="application/x-shockwave-flash" width="560" height="345" allowscriptaccess="always" allowfullscreen="true"></embed></object>
Idea of showing this is not to convince you on the Tunzes (I'm an Ecotech user and a really happy one) what I was think is that with your tank design if you place the powerheads within the confined spaces as your sketch above, you may loose lots of this turbulance due to the center overflow,
If you check this thread (Canadian tank also) http://www.reefcentral.com/forums/showthread.php?t=2060476 you can see how he did his overflow with two dryboxes on each side, I think it's better. Just my 0.02 cents and good luck, nice design on everything.
Hi Bioload,
Great JOB on the 3-d illustrative drawing.
I am out of town and do no have access to my engineering books and computer, but here is some simple information to start with. Also, you do need to find a local professional engineer to look at you site and drawings to properly design and verify conditions. I am up late using the hotel computer to respond promptly.
Could you please tell me a few more details and could you confirm the following?
If I assumed that the tank dimensions are 72"x36"x24" high which is 36 cubic feet and a weight of water of 62 lbs/cf = 2,230 pounds. he glass tank on its own I would estimate 400 pounds, live rock at 1#/CF = 300 Pounds, and another 300 pounds for misc, totals about 3,300 pounds.
Your span indicaed is 11'-3" with conventional 2x8s. Will have to check the span tables to see loading criterea.
you indicate that the tank shall be loaded on only 2 joists but a 36" wide tank/stand, joists at 16" on-centre would have the weight distributed on three. TYPICAL floor loading design is for 20 pounds per square foot of dead load, so 11' x 3' = 33 sq ft x 20 = 660 pounds. The conventional floor joists would be substantially undersized.
The header over the door opening as drawn is a single member and does not show joist hangers installed. The typical joist hangers (you can check out and compare the ones you have to similar ones at Home Depot or Lowes and see what they are rated for. It is unlikely they woulod be rated for much more than 500 pounds, so would be also undersized.
The load transfer from the floor system assembly to the top of walls andfurther down to the footings would also require proper bearing distribution. Normally joists require a minimum bearing of 1.75" or so. Beams require a minimum of 3" to 4.5" of bearing. Placement of columns or vertical members would need to rest on top of the poured concrete wall (if concrete block foundation exists, then larer bearing plates are required) or overtop the footings with sufficient bearing plate size.
Someone mentioned utilizing steel I-beams or wood LVL (engineered wood product) and I would agree. Steel is usually a cheaper alternative, but engineer wood can have its advanage of being able to drill through it and fasten to it easier. Either way, the load should be engineered.
Using two beams installed parallel and within the joist spacing (sized appropriately, like a heavier weight 6" pr 8" dependng what you can fit) and four columns (3"x3"x1/4" wall thickness), where the columns are adjacent and secured to the concrete poured walls with bearing plates (min recommended would be 8"x4"x1/2") where they would rest overtop the edge of the footing under the walls. If you are able to rest upon one of he walls, it needs a minimum bearing depth of 4.5", which you may have difficulty installing.
The height you have to work with in the door way will dictate what type of headering could be installed over the doorway. IF you have the clearance, an I-beam could be possibly installed under and perpendicular to the supporting i-beams in the joist cavity with steel columns on each side of the doorway.
Not sure if that gives you the answer you are looking for, but as an engineer, we can not specify or recommond a solution without knowing all the proper information and have evaluated the on-site situation. Why you shall need to consult and obtain a local professional engineer. At least this post may help guide you in what to discuss with your engineer.
On the road on cell on way to MACNA