<a href=showthread.php?s=&postid=8405946#post8405946 target=_blank>Originally posted</a> by revance
You should NEVER run a 20A receptacle on a 40A breaker because then there is nothing protecting that receptacle from being overloaded and catching fire.
Receptacles do NOT limit the current... if it is rated at 20A and you have it on a 40A breaker, it is possible for you to run 40A through that receptacle and have it catch fire.
As opposed to what i said above.... the NEC DOES NOT ALLOW 20A breakers on a 40A branch!!!
However, the NEC does allow a 15A breaker to be used on a 20A branch circuit!!!
Again the plug configuration is the limiting factor. YOU CAN NOT HOWEVER run a 20A receptacle on a 15A breaker.
In any case, the wire lugs on the receptacle would not handle the #8 wire.... you will find the 30A and 40A receps have larger wire lugs...