With such a device I would never put 120 through it.
It says "nominal VA: 30"
That's volt amps or (Volts x Amps)
So if you put 120 though it you have already exceed 30 VA and you haven't even put a load or device on it yet.
This also explains how extremely small solenoids rated at a mere 3 watts can melt these switches together.
http://www.aquahub.com/store/curingspik.html
Straight from Aquahubs website
<I>
"Let’s say you want your float switch to turn a pump on when the water level in a tank falls below the level of your float switch. Your pump draws 15 watts and your float switch is rated for a 50 watt load. You know that a 15 watt pump could spike to 150 watts (up to 10 times the pump rating) and destroy your float switch, so you would wire the float switch so that it turns on the relay when the water level falls and you would wire your pump to the contacts of the relay"
</I>
These switches are sold for with the intent to have a knowledge of how to use them.
Just because someone sells them, does not make the fit for an unsafe purpose.
While yes there are heavy duty Float switches, these are not one of them.
I also checked the wire on those switches. They are not rated for 120volts
AND
It's only 20AWG wire which IS NOT LEGAL in the USA to be on a circuit breaker of 15 amps (most homes) or even worse a possible 20 amps.
I'm actually starting to work on an entire MARS meeting with the sole subject being "Electrical Safety in the Aquarium Hobby"
They wanted me to have this together by next meeting, but I told them I needed more time to get together a really good presentation. So it will be either March or April's meeting
<b>
I will actually be drinking a glass of water with a 120VAC cord in the glass, plugged in, in the water.
This will be one meeting you won't want to miss!
</b>
I used to teach for an electrician school "WECA" here in Sac.
~Steve~