My current program in the making..

IRISSERVICE

Member
Any tips?


MH1$= Metal Halide Center
MH2$= Metal Halide Left
MH3$=Metal Halide Right
RLT$=Refugium Light
MON$=Moon Light
CF1%=Cooling Fan Center
CF2%=Cooling Fan Left
CF3%=Cooling Fan Right
CHL%=Chiller
HTR%=Heater
WVE#=Wave Box
CO2&=C02 Solenoid
CFP&=Caclium reactor feed pump
CRP&=Calcium reactor Recirc Pump
KMP&=Kalk Mixing Pump
UVL$= UV light
OZN&=Ozone
ROW&=RO water
ALM&=ALARM

Pre light leds
If Time > 17:30 Then MON ON
If Time > 18:31 Then MON OFF

Center Metal Halide 20k
If Time > 18:30 Then MH1 ON
If Time > 00:30 Then MH1 OFF
If Power 010 Then MH1 OFF
If Time > 18:30 Then CF1 ON
If Time > 00:40 Then CF1 OFF
If Temp < 77.0 Then CF1 OFF
Max Change 010 M Then CF1 OFF


Center Metal Halide left 14k
If Time > 19:00 Then MH2 ON
If Time > 23:30 Then MH2 OFF
If Power 011 Then MH2 OFF
If Time > 19:00 Then CF2 ON
If Time > 23:40 Then CF2 OFF
If Temp < 77.0 Then CF2 OFF
Max Change 010 M Then CF1 OFF


Center Metal Halide right 14k
If Time > 19:30 Then MH3 ON
If Time > 00:00 Then MH3 OFF
If Power 012 Then MH3 OFF
If Time > 19:30 Then CF3 ON
If Time > 00:10 Then CF3 OFF
If Temp < 77.0 Then CF3 OFF
Max Change 010 M Then CF3 OFF

After light leds
If Time > 00:30 Then MON ON
If Time > 01:31 Then MON OFF

Refugium Light
If Time > 00:01 Then RLT ON
If Time > 18:30 Then RLT OFF

Chiller
If Temp > 79.8 Then CHI ON
If Temp < 77.8 Then CHI OFF

Heater
If Temp > 76.5 Then HET ON
If Temp < 77.0 Then HET OFF

Calcium reactor CO2
IF PH > 6.6 THEN CO2 ON
IF PH < 6.5 THEN CO2 OFF
If Time > 00:00 Then CFP ON
If Time > 00:00 Then CRP ON

UV Light
If Time > 00:00 Then UVL ON

Ozone
If ORP < 365 Then OZN ON
If ORP > 375 Then OZN OFF

Kalk Mixing Pump
OSC 005/240 ON/OFF Then KMP ON

Water top off with kalk water
OSC 002/240 ON/OFF Then ROW ON
If Switch1 OPEN Then ROW OFF
Max Change 001 M Then ROW ON

Alarms
If Temp > 80.0F Then ALM ON
If Temp < 75.0 Then ALM ON
If pH > 8.50 Then ALM ON
If pH < 7.90 Then ALM ON
If ORP > 410 Then ALM ON
If ORP < 300 Then ALM ON
If Power 000 Then ALM ON
 
You have your comparisons backwards for your heater.
you have
Heater
If Temp > 76.5 Then HET ON
If Temp < 77.0 Then HET OFF

I believe you'd actually want
Heater
If Temp < 76.5 Then HET ON
If Temp > 77.0 Then HET OFF

And you might want to put in Temp comparisons to turn off your MH's in case your chiller fails. Like
If Temp > 81 Then MH3 OFF
If Temp > 81.5 Then MH2 OFF
If Temp > 82 Then MH1 OFF

And also

If Temp > 79 Then CF1 ON
If Temp > 79 Then CF2 ON
If Temp > 79 Then CF3 ON
 
Good eye... :)

were do you sugest i add them?
I can do the these after each light statement.
If Temp > 81 Then MH3 OFF
If Temp > 81.5 Then MH2 OFF
If Temp > 82 Then MH1 OFF

But far as fan cooling. I did not wan them to stay on all the time..
There above each pendent.. I figured have them come on with lights and stay on for 10 minutes more, but if tank was running cold to shut them down. Any thoughts...
 
My thoughts were to have the fans kick on before the chiller had to run to save on electricity. I can understand not wanting the noise from them though. I wouldn't even have them come on with the MH for 10 minutes since it takes about that long for the MH to even start producing a decent amount of heat.
 