I just assumed that for the max load calculation. I am aware that some of the equipment will only be momentary or sheduled<a href=showthread.php?s=&postid=8255596#post8255596 target=_blank>Originally posted</a> by Reefer90210
Bean, you are assuming ALL 5000 watts are on at the same time and for 24hrs a day to get a huge elec bill..

The electric bill comment was a funny

We can easily add it up with regards to your schedule and come up with a pretty good estimate.Anyways, point is, my electric bill will go up for sure, but I dont think its going to be rediculously high. but we will see.
I think you have the idea. You are not likely anywhere near overloading your MAIN breaker. A clamp on meter at the 2 main service conductors would give you an idea of where you are at (your electrician can tell you if this is something you are not comfortable doing). DOn't make the common mistake of "adding" the listed values of the circuit breakers in the panel and comparing them to the main. You will find that even a sparsely populated panel will have a total that far exceeds the main breakers value.As for adding a single 50, is that assuming I have enough room in my total load..so if my house is 200, and I am already using all 200, I cannot just add another 50 right? It would have to replace something? Of course if I am not using all of it , it shouldnt be an issue.
Bean