I'm happy to report I finally got an AC3
It'll be replacing my Ranco, Medusa, Pinpoint PH probe, Milwaukee PH controller, and a half dozen timers.
I only have my DC4HD power and one expansion at this point so only a few things are plugged in. I whipped a program together this morning and moved a few things to the unit. Specifically I wanted to test the heat/fan function first as well as two sets of lights. The last to convert is my PH controller as that is the one that frightens me the most
My issue is, currently it's 78.7 and my fan is still on. It should have shut off at 78.9 (is there a <= function?). However, it does show as off status on the AC3. It's plugged into the "O" slot on the 4 port box, which I assume is A3 (and everything else seems to be working).
XX
OX
Note, this is a 2 pronged device, but I didn't see any limitations there in the manual.
AC3 status screen:
Apr 01 2007 20:26:38
Temp pH ORP
78.7 8.55 288
HE1 ON
LT2 OFF
FN1 OFF
LT3 ON
Power Failed: None
Power Restored: None
HE1%-A01 (Primary heater)
LT2$-A02 (One of my 400w lights on my 180)
FN1%-A03 (Fan over the sump)
LT3$-A04 (Expansion box, 500w ballast for 58, 250 MH frag)
If Temp < 78.7 Then HE1 ON
If Temp > 79.0 Then HE1 OFF
If Temp > 79.3 Then FN1 ON
If Temp < 79.0 Then FN1 OFF
If Time > 13:15 Then LT2 ON
If Time > 20:15 Then LT2 OFF
If Time > 13:00 Then LT3 ON
If Time > 21:00 Then LT3 OFF
I only have my DC4HD power and one expansion at this point so only a few things are plugged in. I whipped a program together this morning and moved a few things to the unit. Specifically I wanted to test the heat/fan function first as well as two sets of lights. The last to convert is my PH controller as that is the one that frightens me the most
My issue is, currently it's 78.7 and my fan is still on. It should have shut off at 78.9 (is there a <= function?). However, it does show as off status on the AC3. It's plugged into the "O" slot on the 4 port box, which I assume is A3 (and everything else seems to be working).
XX
OX
Note, this is a 2 pronged device, but I didn't see any limitations there in the manual.
AC3 status screen:
Apr 01 2007 20:26:38
Temp pH ORP
78.7 8.55 288
HE1 ON
LT2 OFF
FN1 OFF
LT3 ON
Power Failed: None
Power Restored: None
HE1%-A01 (Primary heater)
LT2$-A02 (One of my 400w lights on my 180)
FN1%-A03 (Fan over the sump)
LT3$-A04 (Expansion box, 500w ballast for 58, 250 MH frag)
If Temp < 78.7 Then HE1 ON
If Temp > 79.0 Then HE1 OFF
If Temp > 79.3 Then FN1 ON
If Temp < 79.0 Then FN1 OFF
If Time > 13:15 Then LT2 ON
If Time > 20:15 Then LT2 OFF
If Time > 13:00 Then LT3 ON
If Time > 21:00 Then LT3 OFF