Ok lets clarify.
Total load of a power bar must not exceed 15amps.
So to break down further (in general)
Heaters are FINE on the digital bars, depending on what else you have running on the bar also (i,e not exceeding 15amp draw in total on power bar, taking into account all other equipment plugged in).
Chillers are fine depending on the size, but in 99% of cases will not cause any issue, again depending on what else you have running also (see above)
Kidney - Your heaters should be OK, BUT total draw of the power bar must not exceed 15amps so my statement depends on what else you have running on your power bar.
Here is the Watts to AMPS conversion
Convert Watts to AMPS:
AMPS = Watts / Voltage
I = P ÷ E (I=AMPS, P= watts, E = Volts)
Example:
2,300 WATTS = 2300w divided by 120v = 19.1 AMPS
High AMP striking comes from Ballasts and that is what can potentially shorten the life of relay contacts.
The above statements really comes down to common electrical sense and not overloading a single socket on your ring main.
use the calculation above to determine your over all load and make a decision based on that, as it is only the user that knows what they are running and not us.
But if you are running ANY HO ballasts or high draw T5 ballasts, then consider the HIGH AMP bar.