Just to be clear here, and so folks don't walk away with the wrong idea...I have a 3000 watt ups... it will run a long time,
As noted above, the output capacity of the UPS does not equate to its runtime. The output rating indicates the maximum load that the UPS output circuit can handle without going into failure or safety shutdown.
The runtime is determined by the size of the batteries and the current draw of the load. In theory, a 7Ah battery on a 3kVA UPS will provide the same runtime as a 7Ah battery on a .2kVA UPS. In fact, the smaller UPS will likely have a slightly longer runtime dues to a more efficient power management profile for that same 2.kVA load.
In other words, if you have a 3kVA UPS and you are only loading it to 300VA, then you are not running the UPS in the optimum load configuration and will have a shorter runtime at that load level than the same load on a SMALLER UPS with the same size battery.
Not to call you out.. but you need to drop a zero off of that unless we are talking about a "phone switch" in the sense of a CELL site and its amplifiers and backhaul equipment and a 1000% overhead runtimeI have a $100,000 UPS at work designed to run my phone switch for 24 hours... $1000 gets you a generator st HD and will run it as long as you have gas...
I could sell you several new 100kVA ups systems with an entire room full of battery cabinets and enough runtime to keep a data center alive for a week for $100,000