Most houses are build with a minimum of 40 psf for first floor and 30 psf for upstairs. The limit of these pounds per square foot applies to evenly distributed weight. That is the floor is built to hold a total of 40 x square footage. So a 10x10 room can hold 40 X 10 X 10 = 4000lbs.
A 180 gal tank weighs 2400lbs (including stand, sand and rock...). This is 200 psf! However, if the tank is placed perpendicular to joists, then there is 6 feet of tank over joists and that stip of joist can carrry 6 x 10 x 40 = 2400lbs. Normally, this might be of concern. The tank certainly won't fall through, but there will be floor sag. However, 40 is a minimum and there is usually a 1.5 to 2 safety factor. So you would need a minimum of 3600 to 4800 pounds to have safety issues. Anyway, most 1st floors would normally be ~50psf. Now if you were parralel with the joists, you would only be spanning 2 feet of joists...2 x 10 x 40 = 800lbs! The tank is 3 x this weight so even with 50 psf and 2 safety factor this would be unsafe!