Electrical Help?

<a href=showthread.php?s=&postid=8407215#post8407215 target=_blank>Originally posted</a> by revance
BeanAnimal: Thanks

The 20A ones definitely FEEL more substantial.

They may be more substantial.. but the 15A units are rated to be placed on a 20A branch safely.

I prefer the 20A units when I have the choice. I also only by SPEC grade or better receptacles. The consumer grade stuff is junk. The better SPEC, Commercial and Hospital units have much higher leaf counts and contact pressures. This is a big factor in an arc free connection with repeated plug insertion and removal.
 
<a href=showthread.php?s=&postid=8407288#post8407288 target=_blank>Originally posted</a> by BeanAnimal
Well I hate to disagree... but only point 1 is correct!!!

Point 2 is prohibited by the NEC. YOU CAN NOT PUT A 20A receptacle on a 20A branch circuit!!!!! Again this is 210(b) Your an electrician, you know this ;)

(since when?its done every day.)

Point 3 What can I say.. but I disagree. You can run 12/3 and use (2) non handle tied breakers. If you use a double pole breaker, then a faulting device on one leg will bring the entire tank down!!!!

(who said use a double pole breaker.he would need two 20A single pole breakers)


I opted not to tell the OP to use non tied breakers because we would then have to get into the discussion of ensuring that both breakers were not on the same leg. If he puts them on the same leg, then he overloads the neutral.

(well he doesnt need to use a two pole breaker,so he should have been informed.he will need two 20a single pole breakers to do this correctly.the black wire on the A phase and the red wire on the B phase.)

Lastly, DO NOT USE GFCI breakers. If a device faults it will bring everything on that GFCI down. YOU DON'T WANT THIS!!!!

The best thing to do is use multiple GFCIs on each branch. That way each device is isolted from the next. A faulint device will only trip its own GFCI outlet and leave the rest of the tank running.

(the last two statements contradict themselves so im not sure where your going with this either.)

Remember a lot of our loads (ballasts and large pumps) tend to cause nuisance GFCI tripping.



Bean


i was trying to save the guy some money and aggravation,so take it for what it is worth.
 
Point 2 is prohibited by the NEC. YOU CAN NOT PUT A 20A receptacle on a 20A branch circuit!!!!! Again this is 210(b) Your an electrician, you know this

(since when?its done every day.)
Well the 20A branch was a typo. In any case you said that a 20A receptacle can be put on a 15A branch circuit. That is patently false and prohibited by the NEC. That is why my comment was in regards to. (Your point #1)
Point 3 What can I say.. but I disagree. You can run 12/3 and use (2) non handle tied breakers. If you use a double pole breaker, then a faulting device on one leg will bring the entire tank down!!!!

[/i](who said use a double pole breaker.he would need two 20A single pole breakers)[/i]
I addressed that point! You could use an internally tied double pole or two single poles. I addressed why you would not want a double pole AND addressed in the next paragraph why I did not recomend single breakers on a shared neutral circuit. Honestly... the post was short and to the point.

I don't think you read any of the posts here, including my last one. I think you made some comments and have not thought them through or looked at the context!
I opted not to tell the OP to use non tied breakers because we would then have to get into the discussion of ensuring that both breakers were not on the same leg. If he puts them on the same leg, then he overloads the neutral.

(they cannot be on the same leg using 12/3 so im not sure where your going with this.one is one the A phase and one would be put on the B phase.)
Didn't I just say that?
Lastly, DO NOT USE GFCI breakers. If a device faults it will bring everything on that GFCI down. YOU DON'T WANT THIS!!!!

The best thing to do is use multiple GFCIs on each branch. That way each device is isolted from the next. A faulint device will only trip its own GFCI outlet and leave the rest of the tank running.

(the last two statements contradict themselves so im not sure where your going with this either.)
Your joking right? I don't think the statements could be any more clear. I am not sure if it is a lack of reading comprehension or electrical knowledge that is at play here.... but I am baffled by a lot of your statements.

Let me try again.

1) You said it was OK to put a 20A breaker on a 15A branch circuit. The NEC prohibits this.

2) You said the best way to do this would be to use 12/3 (a shared neutral circuit). I said that in order to do that, the OP would have to either:
A) use a double pole breaker which would cause everything in the tank to shut off if a device on EITHER LEG of the breaker faulted. This is not a good idea for an aquarium that has living things in it.

B) use single pole breakers. The problem here is that the OP would have to ensure that those breakers were NOT ON THE SAME service leg. This is not something you want a first time DIY guy messing with. If he did put them on the same leg, the neutral would become overloaded, as the currents sum instead of canceling.

3) You said to use a GFCI on EACH branch circuit and tie multiple outlets to those GFCIs. I said that a better plan would be to use MULTIPLE GFCIs on EACH branch circuit instead of a SINGLE GFCI on each branch circuit. I also added reasoning as to why NOT TO USE GFCI breakers.

I said it would be good to use MORE THAN ONE GFCI on a SINGLE BRANCH CIRCUIT to isolate each pice of vital equipment. In other words a GFCI receptacle for the RETURN PUMP, another GFCI receptacle for the HEATER, another GFCI receptacle for the Skimmer, another GFCI receptacle for the Closed Loop Pump, another GFCI receptacle FOR EACH lighting ballast.

The reasoning is VERY simple. If everything is plugged into a single GFCI protected outlet, a single faulting device will cause the GFCI to trip and therefore de-energize ALL of the equipment on the tank. Again this is a VERY BAD thing with regards to living critters. Instead with multiple GFCIs per circuit, a single faulting device will have no effect on the other devices on that branch circuit.

Bean
 
you can do what ever you please but your ins will not cover it if it is the cause of a fire, and any electrician wouldn't do that if you want 3 or 4 recepticals on seperate breakers get like some nmd 90 12/3 and do two runs of it or if you can run rigid pvc pipe or emt pull in all the circuits you want but remember only 1 circuit per phase can go on 1 neutral. 1 hot from phase "a" 1 hot from phase "b" on 1 neutral. but 2 15 amp recepticals should be sufficient for most setups at work we never use anything less that #12 its rated for 20 amps in canada in the code book you could run #10 if your worried about voltage drop but any larger would be rediculus
 
<a href=showthread.php?s=&postid=8409389#post8409389 target=_blank>Originally posted</a> by nikygm
but remember only 1 circuit per phase can go on 1 neutral. 1 hot from phase "a" 1 hot from phase "b" on 1 neutral.

You can put more than (1) circuit per phase on a single neutral. I beleive the code allows for this. The neutral has to be sized accordingly. It is done in commercial work all the time... it is a mess for homeowners and NOT a good habbit to get into.

The subject of shared neutrals keeps coming up. They are a nightmare for home owners and should not be used. An open in the neutral can cause a serious problem (the two circuits are now in series with each other).

Secondly if the breakers are not TIED, then the unsuspecting homeowner can get shocked if working on a circuit when only one of the shared breakers is tripped.

We can make a whole laundry list of why shared neutral circuits are not suitable for residential use....

Bean
 
Bean,

I agree with your post on multiple GFCI outlets on a single circuit. However I don't think that most people understand how to wire that correctly. Most people will wire in the GFCI outlets in series which will cut off any outlet below the tripped outlet. To isolate each outlet, they need to be wired in parallel so that when an individual outlet trips, all the other outlets are not affected. I am not an electrician so I may have described that awkwardly. Could you give a proper description of how to wire these outlets?

If I remember correctly, they usually describe it with the instructional insert for the outlet. But who ever reads those.
 
If they wire those GFCI's in series they're going to have worse problems than just the GFCI tripping and taking out the whole circuit. ;)

You're right though, if they don't wire it correctly, it won't work correctly.

That's the whole point of the thread.
There's alot of DIY that can be done by trial and error, worst case scenario, you wipe out your tank or end up spending more than you would have if you bought a product off the shelf.

With regards to electrical stuff like this.. worst case scenario, you burn your house down and kill your whole family.
 
<a href=showthread.php?s=&postid=8411273#post8411273 target=_blank>Originally posted</a> by Acipenser
Bean,

I agree with your post on multiple GFCI outlets on a single circuit. However I don't think that most people understand how to wire that correctly. Most people will wire in the GFCI outlets in series which will cut off any outlet below the tripped outlet. To isolate each outlet, they need to be wired in parallel so that when an individual outlet trips, all the other outlets are not affected. I am not an electrician so I may have described that awkwardly. Could you give a proper description of how to wire these outlets?

If I remember correctly, they usually describe it with the instructional insert for the outlet. But who ever reads those.


Since this was my post to begin with I thought I would respond to this one. I do understand the difference between parallel and series and how they should be wired. Thanks to Bean when I ask a question I not only get an answer but an explanation too.
:rollface: :rollface:
 
<a href=showthread.php?s=&postid=8411273#post8411273 target=_blank>Originally posted</a> by Acipenser
Bean,

I agree with your post on multiple GFCI outlets on a single circuit. However I don't think that most people understand how to wire that correctly. Most people will wire in the GFCI outlets in series which will cut off any outlet below the tripped outlet. To isolate each outlet, they need to be wired in parallel so that when an individual outlet trips, all the other outlets are not affected. I am not an electrician so I may have described that awkwardly. Could you give a proper description of how to wire these outlets?

If I remember correctly, they usually describe it with the instructional insert for the outlet. But who ever reads those.

I guess I should have pointed out that they must be in parallel. As you and others have mentioned, placing them in series (Line to Load, Line to load, etc) will create all kinds of strange problems.

Your description is also correct. They outlets will all be wired in parallel. In other words each one will be have its LINE side connected to the 120V circuit, nothing connected to the LOAD side.

As usual, if this sounds at all foreign to anybody contemplating such a setup.... ask for some qualified help from a friend or hire an electrician.

Bean
 