Well I've been debating on getting it but now that I did wish I would have done it sooner. This thing is freaking awsome. I am now able to keep the tanks temp to only a 1deg change. Before the chiller would go from 80.5-78.5. Now its from 80-79. Its so cool I was able to get rid of two power strips. I also have a way to contron the tanks ph and the Ca reactors ph independantly from each other. Oh and the temp probe is alot better then the chillers built in probe. Here is my programing so far. Let me know if ther is something wrong. Thanks to Gcarroll for pushing my in the right direction
IF TIME IS 12:00 THEN ATI A06 ON
IF TIME IS 21:00 THEN ATI A06 OFF
IF TIME IS 12:30 THEN MHR A01 ON
IF TIME IS 20:00 THEN MHR A01 OFF
IF TIME IS 13:00 THEN MHL A02 ON
IF TIME IS 20:30 THEN MHL A02 OFF
IF TEMP IS >81.5 THEN MHR A01 OFF
IF TEMP IS >81.5 THEN MHL A02 OFF
IF TEMP IS >80 THEN CHL A03 ON
IF TEMP IS <79 THEN CHL A03 OFF
IF TEMP IS >79 THEN FAN A04 ON
IF TEMP IS 78.5 THEN FAN A04 OFF
IF PH IS >8.15 THEN CO2 A05 ON
IF PH IS <8.10 THEN CO2 A05 OFF

IF TIME IS 12:00 THEN ATI A06 ON
IF TIME IS 21:00 THEN ATI A06 OFF
IF TIME IS 12:30 THEN MHR A01 ON
IF TIME IS 20:00 THEN MHR A01 OFF
IF TIME IS 13:00 THEN MHL A02 ON
IF TIME IS 20:30 THEN MHL A02 OFF
IF TEMP IS >81.5 THEN MHR A01 OFF
IF TEMP IS >81.5 THEN MHL A02 OFF
IF TEMP IS >80 THEN CHL A03 ON
IF TEMP IS <79 THEN CHL A03 OFF
IF TEMP IS >79 THEN FAN A04 ON
IF TEMP IS 78.5 THEN FAN A04 OFF
IF PH IS >8.15 THEN CO2 A05 ON
IF PH IS <8.10 THEN CO2 A05 OFF