I just purchased a ACIII Pro for a 180 Gal AGA. I just purchased a GEO Calcium Reactor and Nielsen Reactor - I am also new to these pieces of equipment. Please evaluate my program. I have a Pinpoint pH MONITOR for Calcium Reactor Effluent and I will be using the Neptune to CONTROL the CO2 Solenoid based on TANK pH.
ACT = Actinic lights
LT1 = Outside Halide lights (I have a 72" Maristar)
LT2 = Center Halide
NRX = Nielsen Recirculation pump
CRX = CO2 Solenoid
FAN = Canopy Fans
HET = Heater
If time > 1200 then ACT = ON
If time > 2400 then ACT = OFF
If time >1700 then LT1 = ON
If time < 2330 then LT2 = OFF
If time > 1800 then LT2 = ON
If time < 2230 then LT2 = OFF
If temp > 80.3 then FAN = ON
If temp < 80.3 then FAN = OFF
If temp < 79.7 then HET = ON
If temp > 79.7 then HET = OFF
If temp > 81 then LT2 = OFF
Max Change 45 M
then LT2 OFF
If temp > 81.5 then LT1 = OFf
Max Change 45 M
then LT1 OFF
If pH < 8.2 then CRX = OFF
OSC 10/50 ON/OFF
then NRX ON
If pH > 8.4 then NRX = OFF
Please feel free to comment on program/set points as I am new to most of this equipment. Thanks.
ACT = Actinic lights
LT1 = Outside Halide lights (I have a 72" Maristar)
LT2 = Center Halide
NRX = Nielsen Recirculation pump
CRX = CO2 Solenoid
FAN = Canopy Fans
HET = Heater
If time > 1200 then ACT = ON
If time > 2400 then ACT = OFF
If time >1700 then LT1 = ON
If time < 2330 then LT2 = OFF
If time > 1800 then LT2 = ON
If time < 2230 then LT2 = OFF
If temp > 80.3 then FAN = ON
If temp < 80.3 then FAN = OFF
If temp < 79.7 then HET = ON
If temp > 79.7 then HET = OFF
If temp > 81 then LT2 = OFF
Max Change 45 M
then LT2 OFF
If temp > 81.5 then LT1 = OFf
Max Change 45 M
then LT1 OFF
If pH < 8.2 then CRX = OFF
OSC 10/50 ON/OFF
then NRX ON
If pH > 8.4 then NRX = OFF
Please feel free to comment on program/set points as I am new to most of this equipment. Thanks.