The newest osmolator has the following logic program-
Water drops below the optic sensor, green led blinks until low level is detected for 5-10 seconds (idea is to ignore a wave of momentary turbulence).
Yellow led kicks on and pump is on
Green led comes on with yellow led for 8-15 seconds, water is level but a deliberate overfill is being added, this would not be cumulative since it would not do this again until the water was again below the sensor.
If the water overfills to where the float switch is raised it would sound an alarm and the red too high led is on, the system is shut down until the float lowers
If top off was attempted for 10 minutes and not achieved,the red too low led is on, the system is shut down until power is manually cycled. (The logic is your tank is leaking or there is no water in the reservoir and nothing good can come of continuing to run)
If both too high and too low leds are on and blinking, something has bridged the contact, either water damage or a magnetic field and the system is shut down until serviced, a signal conflict can also cause this, such as a raised float caused by a magnet or snail and a low water level detected by the optic sensor.
If, you are topping of to your sump, the manual generally outlines sensors in the sump, top off hose to the tank as the safest as a siphon is virtually impossible in this scenario, the low head pressure could allow more water to be added in the 10 seconds, the solution is simple, just turn down the pump with the internal potentiometer.
It could also be that a bubble or something affected the sensor and caused this 1/2" change, if their are a lot of bubbles present, the osmolator sensors should be moved to a position free of bubbles. This sensitivity to bubbles is diminished after a few days of use, but is quite pronounced when the sensor is new, new plastic repels water and attracts air and until it is "seasoned" and has a biofilm on it, it will be very sensitive, a hot soapy water rinse does help.