Mmm u could try having ur lights on sep timers ? Make sure they turn on independently. Or unit is one cord ?
They're both run by Apex, on separate outlets. They don't turn on at the same time.
Most breakers are slow-acting (allowing very brief periods of high-amperage so that devices can start up). That's why it doesn't trip when they start. However, it sounds to me like either: A) There's something else on that same circuit (e.g. refrigerator) and everything is fine until that thing turns on and pushes the amperage over the limit. Or... B) The combination of the lights and other equipment is pulling more than you think, or more than the label says they should - you can check this with a Kill-A-Watt. Or ... C) The breaker is old - sometimes they will trip at less than their rated current if they're old.
Of those I'd say A or B is the most likely.
The only other thing on the circuit is a couple of small lamps and my QT tank. I'm monitoring amperage through Apex's display, which I assume to be reasonably accurate.
Given it's a leased apartment, I'm a bit hesitant to swap out the breaker. I don't want to end up in trouble.