Double checking my Tunze 6105.5 safety connector setup in preparation for Hurricane Irma and Jose. Supporting both a 75gal and 90gal, this is my battery back-up as follows:
12V 35Ah Duracell Deepcycle SLA battery + Tunze safety connector will run the return pump Tunze 1073.05 during any power failures automatically but for how long?
Adding a 2nd or 3rd safety connector could run more equipment like the Tunze controller 7000 and Tunze 6055/6095 wavemaker(s) but I'll do with just the return pump for now maybe adding the controller too... I also have a battery operated air pump + air-stone combo.
So Tunze pumps are engineered to allow for the choice to run their DC pumps via their jumpers at either 12v, 18v or 24volts.
I run all my controllable pumps at 24v.
If I add another 12v 35Ah SLA battery and run them in "series" achieving the 24v step-up in capacity... then add 7000 controller + additional pump(s). Is 2 batteries overkill or worth the additional estimated runtime?
My return pump's max energy consumption at 24 V equals a max. of 43 watts. I'm unsure of the realtime power draw.
10x(Battery Capacity in Amp Hours) / (Load power in Watts)
_________________________________________
= Run time in hours
10x(35Ah)/43watts=Run time in hours
Series Option: 10x(70Ah)/43watts=Run time in hours
I'm double checking with Roger and/or the folks in the thread for feedback /suggests on this setup?
Thank you!