Now on to the mix tank. It has three sensors. A low sensor, a full sensor and a pressure sensor. Below is the setup for the Mix Low sensor. The type is sense port since it is a float switch. The sense mode is water level. The sense port is on a Control 2 in the garage. The notification level was set to orange. alert when dry is turned on. So it will send an alert when the mix tank is low. This was a new feature added to the firmware during the time I was setting this up. Since this has not changes since then I used recent screenshots on this and the next one. Also I forgot to mention until now I had to flip the float on some of the float switches so they would read dry when the water level was below the float and wet when it was above the float.
Below is the Mix Full sensor setup. It also uses a sense port and is also a float switch. It is on the same Control unit as the Mix Low sensor above. The notification level was set to none on this.
Below is the water level input which uses a pressure sensor. It is only for a general idea of the water level in the tank. The input type is 0-10v. The 0-10v input mode is Analog. The 0-10v input used is on a Control 4 in the garage. It is input 3. Scale factor is 10 and offset is 0. There is an offset and gain adjustment on this sensor so no need to change them here. The DI and fresh saltwater uses a different sensor and these settings are different for them. The Data Type is Generic.
Below is the Mix Low output. It uses the generic output type. It has a single input. The input is the Mix Low input. This output is on when the Mix Low input is dry. The output device is none. This output is used for logic only. This output is also used in the mix ready logic to clear mix ready since the mix tank is low.
Below is the Mix Full output. It also uses the generic output type and uses only one input. The input is Mix Full. This output is on when the input is wet. It also has no output device selected.
Next is the Mix Fill Latch output. It is used to latch the mix fill output on once the Mix Low output turns on. It uses the Combiner type output. Input 1 is the Mix Low output. It is not inverted. Input 2 is the Mix Fill output. In is not inverted. The Combiner Mode is OR. So if either input is on the output will be on. This output has no output device selected since it is only used for logic.
Below it the mix fill output. It uses the combiner output type. Input 1 is the Mix fill latch. The second input on the mix fill latch is this output. So once this output turns on it causes the Mix Fill latch to stay on keeping this output on unless input 2 is on. Input two is the Mix Full output. This input is inverted. So when it is off it the same as on on a non inverted input. This uses the AND combiner mode. So input 1 has to be on and input 2 has to be off for the fill output to be on.The output device is a drive port on a Control 2 in the garage. This output depends on the Leak Garage output. The dependency mode is off if on. I switched the leak detectors from the Archon to the Hydros since the last post here. This output combines the AC Leak and RODI leak sensors. AC leak is a leak sensor under the central air conditioner which is on the other side of the wall from the RODI unit. The garage leak sensors were switched over to the Hydros when the screenshot was taken. So if a leak is detected at either it will stop any refill or water transfers in the garage until the leak is resolved. Advanced settings are enabled. A maximum on time is set for 5 hours and 30 minutes. Run past max on time is set to off. If the fill output stays on for 5 hours and 30 minutes it will turn off and send a notification. If it takes that long something is wrong.
Below is the logic schematic for the mix tank refill outputs. It is basically the same as the one for the DI refill except it uses different low and full sensors and drive a different solenoid. That is about it for now for the DI reservoir, fresh saltwater reservoir, Mix tank and RODI control for now. There were some dhanges I get to when I get to that time frame.