Robthorn, I am humbly asking for some guidance here
. I would rather not lock up this compressor as I did to my heat pump once while following some information given to my by a questionable HVAC contractor. I did end up with a very nice Trane 12XL. But that is a long story so here goes what is relevant.
I have a 12oz charge in the system and my data is
High side 170 psi
Suction 38-45 psi not very steady.
Water inlet temp of 82
Temp drop of water in the chiller 2 degrees
Suction line temp 62
Ambient outside temp 73
Tank temp dropped 2 degrees in 40 minutes
My chart shows a superheat of about 28 degrees - but that is based on 400cfm/ton airflow. How does that relate to my waterflow of 1000 gph?
I imagine all of my "indoor" temperatures would be wet bulb. If that is the case, my superheat is more like 43.
How do I calculate my superheat?
Should I just charge to a certain set of pressures?
As you can probably tell, I am not a experienced contractor - I just know enought to be dangerous. But I am really excited about my progress.
Thanks