Handle ties on multiwire branch circuits were not required until the 2008 Code. Very few places are using the 2008 code yet, so very few places have that requirement.<a href=showthread.php?s=&postid=13490100#post13490100 target=_blank>Originally posted</a> by J-Burns
I don't think you should have a double pole breaker feeding 2 seperate circuits as a double pole breaker should have both sides tied together to trip together.
I think you just contradicted yourselfI suspect you new electrician will either remove the clip holding the breaker together or replace it with 2 single pole breakers.
In any case, He mentioned that the 40A breaker in the main panel was a double pole 220V breaker. That would indicate that it IS handle tied. That is perfectly acceptable and the subpanel with the two 20A breakers does not (and should not have) handle ties. Each 20A breaker is a separate branch circuit.