Attached or detached to the building with the main panel... it makes a difference
Lets just talk about a sub panel in the same building.
for a 120/240V sub panel you MUST have a (4) wire feed. That is (2) hot legs (1) equipment ground and (1) neutral.
The NEUTRAL bar in the SUB panel MUST not be bonded to the ground, ground bar or the panel box housing. It MUST be isolated on its own bus bar. This is a MUST.
You DO NOT have to have a MAIN breaker in the SUB panel, but it is a nice option.
The breaker feeding the sub panel MUST have both poles handle tied. This is a MUST.
The breaker feeding the sub (this should be obvious) must not exceed the rated ampacity of the service cable feeding the sub.
On the other hand, it is perfectly acceptable to oversize the feeder and still use a small breaker set to feed it.
The sub can be fed with copper or aluminum wire.
The sub panels physical location falls under the same rules as a main panel.
Now for an isolated building... things get a bit more complicated due to the grounding rules. Let me know if you need info on that.
<a href=showthread.php?s=&postid=15646009#post15646009 target=_blank>Originally posted</a> by H20ENG
Oh and I concur about the forum lately Stu!
Hi ya Steve<a href=showthread.php?s=&postid=15646172#post15646172 target=_blank>Originally posted</a> by Steve 926
IT'S "ALIVE " !!!!!!!!!!!!!!!!!!
Glad to see you back
( still looking for a fine whine on Collins ave )
Steve
I would agree to that also, your right Bean, but most electrical fires start when the power company loses its neutral to your feeder.<a href=showthread.php?s=&postid=15647664#post15647664 target=_blank>Originally posted</a> by BeanAnimal
Frank, you don't bond the neutral in a sub panel becuase if you do then objectionable current flows through the grounding conductors, defeating their purpose. Furthermore, NEUTRAL current flowing over loose connectors in the grounding system (like an EMT connector) can cause severe heating and/or fire. The size of the "ground" with regard to the "neutral" is not what is at issue. The issue is that the panelboard and other bonded materials will ALWAYS be energized and potentially deadly.
The "grounding cunductor" is actually a bonding conductor and is not meant to carry current. It is meant to keep all points of the system at the same potential with regard to EARTH and the BONDING POINT in the main panel.
<a href=showthread.php?s=&postid=15646145#post15646145 target=_blank>Originally posted</a> by BeanAnimal
Yeah I almost fell outa my chair when I read his question... knew it was heading for trouble.
jnarow... you missed a wire. Is the ground hooked to GROUND or NEUTRAL? Or are you only running (1) hot to the sub?