Grounding probes

You will get a lot of opinions both ways. There's even an article from a Georgia Tech professor saying they can actually create a dangerous situation.
All I can do is discuss my exprience. After reading these articles, I was convinced grounding probes were bunk. Then I notices I had some errant current in the tank and in my sump that I couldn't easily isolate. I bought 2 Coral Life probes, put one in my tank and one in my sump, and stray current is gone.
 
It's not gone. It is still there, but you are sending it to ground. Right through your tank.

If you want to see the voltage? Put a resistor in line with the ground probe, and check the voltage drop across it.
 
The voltmeter will not show amperage. The probe simply turns the voltage into current(amperage) by giving a path to ground. Amperage meters are more costly and not usually used by aquarists.

Even a gfci wont sense the current(amperage)loss until some of it goes to ground and fails to return. Even though it trips almost instantaneously when current is lost, the current still has to run to ground( albeit at the speed of light) before it trips.So the further away from the leak the probe is the more tank,pipe, refugia.etc. it will run through before going to ground and tripping the gfci.. Induced voltage those 2 or 3 volts that seem to be in every tank will constantly flow as current the length of the course from the source to the ground and may not trip a gfci.There may be other situations where a gfci wont trip as well. So if a probe or probes are used optimal placement to protect you and your fish is in in my opinion close to (a) device(s) that may be likely to cause a problem such as a power head or heater.

Perhaps some of our friends with electrician or electrical engineering backrounds can chime in.
 
Wow, guess I really stirred the pot up here. My goal is not to cut down on others practices, but to give the correct information on the subject so that others can make their own decisions.

First let’s talk about a GFCI and how it works. There seems to be a lot of miss information floating around.

A GFCI measures the current flow from your hot to neutral (or grounded) conductor. The little round hole in the outlet that the ground prong of a plug goes into is for the “grounding” conductor. There is a HUGE difference. A GFCI has a solid-state device in it that monitors the current going too the device and the current leaving the device. This amount falls within certain limitations. If the GFCI detects an abnormality in this it trips. It has NOTHING to do with the ground prong, plug, wire, etc.
Example:
If you have an old house with the old two slot outlets, you can change that outlet out to a GFCI and it will work. Is that code, no, but it will work properly. Note: I do not recommend this.

Next

I’m going to go into the whole “double insulated” thing a little deeper. I’ll use a corded drill for an example.
If you have an ALL-plastic drill housing it is considered to be double insulated. This is because there is no reasonable way for any current carrying parts of the drill to come into contact with the operator. This means that even the chuck of the drill will be coated in plastic OR be separated from the motor by plastic gears, etc.

Now if you have a drill with a metal housing or a combination of metal/plastic you will have a grounded plug. This is so that if, no matter how slim the chance, one of the current carrying parts of the drill comes into contact with the housing the fault current will be directed to the grounding conductor of the circuit and not the user.

UL, CPSC, and other test facilities around the world favor the double insulated method. It’s safer for the layperson. Now just because something is double insulated dose not make it foolproof. If something catastrophic happens, say a heater breaks; it’s not going to be good, like in cczarnik’s case. Chances are that it wasn’t the current in the tank that kill it, but the coating on the heater elements and the heater guts breaking down that polluted the tank. And I’d bet a 6 pack of your favorite drink that if he had a ground probe the same thing would have happened. On a side note, sorry to hear about that.

Having a ground probe will not trip a GFCI if there is a bad device in your tank. They just don’t work that way. On the other hand, a arc fault breaker is, but that’s a new topic.

Moving on.

Stricknine said:
As per Canadian and National electrical code (CEC in Canada, NEC in US), all metal in an electrical system must be grounded because it is conductive, and this rule should pass on to water as it is the same concept. In addition, in electrical code books there is a TON of grounding requirements for swimming pools: all water, metal, and current carrying material MUST be grounded within a certain radius of the pool SO if there is a fault it is a tripped circuit and not a live wire.

Last I checked you don’t ground a swimming pool. You are required to ground the equipment FOR a swimming pool. That way if the equipment for the pool fails and causes a fault it has a good grounding source to go to and doesn’t go to the pool or its occupants for it. That’s a bad comparison anyway. You don’t put electrical devices in a swimming pool with the exception of built in light’s etc. What you have to understand is that it’s not about grounding the water, it’s about grounding the device and preventing the stray voltage going to the water. The water is a pool is grounded naturally by the concrete, liner, etc. that incases it.

Stricknine said:
- If you have faulty equipment and don’t have the tank grounded, you will never know. Ground the tank and the GFI will pop within milliseconds of the live wire hitting the surface.

Nope.
First, your tank is not a means of circuit protection. Second, it won’t trip the GFI unless both the hot and the neutral of the same circuit are put in the water. GFI’s have nothing to do with the ground. Third, you would probably trip the breaker with a grounded tank and a hot wire put into it.

In closing, AC current in a tank is not going to randomly zap fish and corals. Electricity is looking for one thing, ground. The earth is the only thing that has enough area to dissipate it. It’s when a fish, coral, people, etc get in the way of electricity getting to ground that there’s a problem.

I am confident that if you put a live wire in an isolated tank that there would be no ill effects. If there is nowhere for the current to go, then there is no potential. It’s no different than if you have an extension cord plugged in and the other end is lying on your living room floor. It doesn’t randomly zap people walking around. It’s only if someone comes in contact with the current carrying conductors and provides a source for ground that you’d have a problem.

Like I said before, I’m just stating the facts and honestly trying to help. I don’t want any hard feelings. Let’s face it; no one wants to see anyone get hurt.
 
Last edited:
58 merc, Thanks for your posts. I am getting most of it but still have trouble understanding this part.

"Having a ground probe will not trip a GFCI if there is a bad device in your tank.They just don't work that way."

If the gfci detects abnormalities in hot/ neutral ,in /out flow, then why wouldn't it detect current lost to ground from a faulty device via a ground probe or me if I'm grounded and touch the water with no probe?

BTW I use plug in gfcis for appliances in the water without using any probes. Will this offer protection to me should I inadvertently touch the water with stray voltage in it and be grounded?Or touch the water and inadvertantly touch a metal light canopy with or without a short?Is there a way to protect against a heater seal failing other than guesswork and periodic heater replacement?

Thanks
 
The Simple
-------------

- Have a GFCI for each wall outlet in use. This will prevent electrocution, with or without a grounding probe and with or without ground.

- A grounding-probe (with GFCI) can be a good idea, but it requires you have ground. :)

- Grounded surge-protectors are also a good idea, but they must be kept dry, with or without GFCI.

-------------
The rest is mostly endless theory.
 
Uugh...

"A GFCI measures the current flow from your hot to neutral (or grounded) conductor. The little round hole in the outlet that the ground prong of a plug goes into is for the “grounding” conductor. There is a HUGE difference. A GFCI has a solid-state device in it that monitors the current going too the device and the current leaving the device. This amount falls within certain limitations. If the GFCI detects an abnormality in this it trips. It has NOTHING to do with the ground prong, plug, wire, etc.
Example:
If you have an old house with the old two slot outlets, you can change that outlet out to a GFCI and it will work. Is that code, no, but it will work properly. Note: I do not recommend this."

***For the first part I agree, for the rest is INCORRECT. If you do not have a ground, the GFCI (ground fault interuptor) is useless. Without the path to ground it is no different than a standard receptacle. As stated above, the GFI rec. measures the in and out current. Think of the wiring diagram as a " Y ". The top left is 'HOT", the top right is "NEUTRAL". and the bottom is "GROUND". If you touch between hot and neutral, you become a light bulb so to speak. Electrically speaking this is OK (for this example) because the current released by the "HOT" wire is equal to the current return on the "NEUTRAL" wire. If there is a fault between the "HOT" wire and "GROUND", neutral is going to say ***, current in and not out through me?...and trip the "GFCI" due to the GROUND FAULT.(circuit interrupts)

"You are required to ground the equipment FOR a swimming pool. That way if the equipment for the pool fails and causes a fault it has a good grounding source to go to and doesn’t go to the pool or its occupants for it. "

***This is exactly my point. Just because we commonly use plastic housings in the hobby doesnt relieve the risk of a fault. In a pool, the metal equip is used as gnd, which in turn grounds the water (or at least any water near the equipment) quote:"if the equipment for the pool fails and causes a fault it has a good grounding source to go to". The aquarium requires this ground as well.

"Second, it won’t trip the GFI unless both the hot and the neutral of the same circuit are put in the water. GFI’s have nothing to do with the ground"

***FALSE. GFCI (ground fault circuit interuptors) have EVERYTHING to do with ground. It is the entire premise! If hot and neutral are put in the water this becomes a overcurrent issue in which the overcurrent protecting device (breaker or fuse) will trip due to high current caused by the waters low resistance...BUT if there is a fault in a device which leaks a current to ground, again "neutral is going to say ***, current in and not out through me?...and trip the "GFCI".


Long post short, and stated by others, GROUND THE WATER, and also USE A GFCI. I wish I could find it, but had a similar post with a guy constantly getting shocked by his tank, despite having a GFI outlet installed. (old house, not grounded) In the end he pounded a ground rod outside the house, ran the ground (or reference point) to the tank and voila! problem solved. (not the recommended method, or code compliant way about it but...).

And for the record, I may not be a part of the "brotherhood", but am a red seal-interprovincial certified journeyman electrician.
 
<a href=showthread.php?s=&postid=14067418#post14067418 target=_blank>Originally posted</a> by reefergeorge
It's not gone. It is still there, but you are sending it to ground. Right through your tank.

If you want to see the voltage? Put a resistor in line with the ground probe, and check the voltage drop across it.

I realize the stray voltage isn't gone, that the faulty device is still leaking. My point was, after reading various articles I was convinced that a GP would make stray voltahge more dangerous, but what I found is that I no longer get the "tingle" when my hand is in the tank.
 
One problem I've found with GFCIs is that they trip with a power outage without exception. Accordingly, once the power comes back on, power is not restored to the equipment until I reset the GFCI. This is a real problem when that equipment is a return pump or a heater, which is why I stopped using my GFCI's. I really wish I knew a solution to this, because I am uncomfortable not using them. If anyone else has a fix for this problem, I would love to hear it.
 
<a href=showthread.php?s=&postid=14068153#post14068153 target=_blank>Originally posted</a> by stricknine
If you do not have a ground, the GFCI (ground fault interuptor) is useless.

Absolutely false.

The neutral wire and the ground wire are not at all the same. And it doesn't matter how the current finds ground, if it does, then neutral and hot don't match, so it flips.

A ground line is needed for your surge-protectors. Gives a safe place to send any surge. If your surge protector plugs into your GFCI, which it should, then you'll want to have grounded GFCI. But GFCI will keep you safe even without a ground line.

Done. :]
 
<a href=showthread.php?s=&postid=14068153#post14068153 target=_blank>Originally posted</a> by stricknine
had a similar post with a guy constantly getting shocked by his tank, despite having a GFI outlet installed. (old house, not grounded) In the end he pounded a ground rod outside the house, ran the ground (or reference point) to the tank and voila! problem solved. (not the recommended method, or code compliant way about it but...).

Right. He was getting shocked. As opposed to electrocuted. He was not a path to ground, nor was there one present. Had he been standing barefoot in a pool of water, then his GFCI would flip and save his life. Don't need a ground line for that. He would have been the ground line. That is what the fault interrupt is all about. It interrupts ANY fault to ground. Doesn't matter what it is. If it subtracts from the neutral line, then the GFCI flips.

Okay, now I'm really done. :]
 
If someone would take a tank with specimens that need to be euthanized (a diseased fish, bad hitchhikers, etc), intentionally energize a tank, and document the results maybe it would demonstrate for all the value of a ground probe and gfci. Without both, you're betting your tank (and potentially your life) on the integrity of the plastic and glass housings of your electrical equipment. I took that bet and lost.

I have some thoughts on a series of trials that would compare the effects of (1) non-energized copper exposure, (2) energized copper exposure, (3) energized non-copper exposure, and (4) long term effects of introduced low level current through a series of probes.

If we empirically gather this data, perhaps it could put the whole debate to rest (although I doubt it). Whoever ran these trials would definitely get a good spanking on the husbandry forum, and I really don't want to be known as the guy who electrocutes fish (at least not intentionally).
 
<a href=showthread.php?s=&postid=14068243#post14068243 target=_blank>Originally posted</a> by abulgin
One problem I've found with GFCIs is that they trip with a power outage without exception. Accordingly, once the power comes back on, power is not restored to the equipment until I reset the GFCI. This is a real problem when that equipment is a return pump or a heater, which is why I stopped using my GFCI's. I really wish I knew a solution to this, because I am uncomfortable not using them. If anyone else has a fix for this problem, I would love to hear it.
:) Hi, Mine don't do that, neither the wall outlets,nor the plug ins. Don't know why yours do unless a device on the circut is casuing it when started up. I had a pc light that used to cause tripping when it started.
 
<a href=showthread.php?s=&postid=14068243#post14068243 target=_blank>Originally posted</a> by abulgin
One problem I've found with GFCIs is that they trip with a power outage without exception. Accordingly, once the power comes back on, power is not restored to the equipment until I reset the GFCI. This is a real problem when that equipment is a return pump or a heater, which is why I stopped using my GFCI's. I really wish I knew a solution to this, because I am uncomfortable not using them. If anyone else has a fix for this problem, I would love to hear it.

Until reading this I thought I thought physical/mechanical science was an exact science- based on true concepts--- now I am confused.:D It is a scarry thing when well qualified electricians can't agree on the same principles.

Abulgin--I had an electrician wire two receptacles to my basement fish room with a separate line going to the main box. He did not put the gfci's in the receptacles but rather put one trip switch at the main circuit box.
This has worked before--a couple of years a glass heater broke in the sump and it knocked out the circuit--tripped the switch at the box.

I was also told that you only need one gfci on one line even if you have have a dozen receptacles on the same line???
 
These GFI threads can go on forever and everyone is correct some of the times.
I have been an A Rated journayman IBEW electrician Foreman for forty years and I remember when the things were invented and the representative from the company came to the jobs to explain their function.
There is a reason that all indoor bodies of water are supposed to be grounded and swimming pools have very strict grounding codes. I personally would not go near an ungrounded swimming pool or let my family near one. I have been severly shocked more than most here just by my years in the trade.
It is true that in some circumstances a ground probe can be dangerous but in far more instances it will save your life.
I can go into examples of what powerhead I am holding with my feed on dry floor with one hand around a wet cat while whistling Swanni River but the fact is that the codes were written for a reason although they do not mention fish tanks sopecifically.
All devices should be grounded weather they be toasters, light fixtures, TVs or nuclear reactors. That third prong on an outlet was not always there, they came out about 45 years ago to protect you. If nothing is connected to it, it is just a waste of wiring. I have been shocked almost to the point of not being here before they invented GFIs (trade name) or as you call them here GFCIs when powerheads were aluminum and not submersible or when lights fell into the water. It is not pleasant.
I have also had lights fall in the water when I have had GFIs and ground probes installed and I never got a shock.
We all know that the thing detects currents on the hot and neutral. We can easily be the load between the hot and the neutral but if there is a ground probe you will not be shocked, killed, sunburned or anything else.
Good Bye have a great day.
 
<a href=showthread.php?s=&postid=14066241#post14066241 target=_blank>Originally posted</a> by reefergeorge
titanium.
edit- posted at same time.

Every time GPs come up we always have the same arguments. The only thing that makes sense to me, and has been posted before. Is to put the GP on a switch, and switch it on before you reach in the tank. That way the fish won't be bothered by any constant current, and it something is faulty, it will ground out before you reach in.

yep we came to that conclusion several months ago when we all had a big chat about it back then, i cant remember what thread it was or what forum, but after several arguments for and against i think reefergeorges switch idea was agreed as a good 1, im not going to get involved too heavily with this thread as ive been involved in a few now and it can get outta hand, all i will say is over here we bond everything to ground and protect by RCD (gfci) and use multiple units, the reason for multiple units is nusience tripping, example is in a house over here we have a power circuit protecting several socket outlets, there can be 10 different things plugged in, and when all on the trip will go because of a collective excessive current to earth, all appliances are fine and they can be swithed on randomly but the same happens, so we would use 3 or 4 seperate circuits to the appliances, this way theres no nusience tripping, but the gfci is still in the on position but ready to trip under fault conditions, my conclusion would be several gfci if its possible, and as mentioned a switch on the probe, hopefully reefergeorge can find the link somewhere which discussed this, there are a few mind so im not sure which one to look for, good luck with the thread and no arguing:lol:
 
<a href=showthread.php?s=&postid=14068674#post14068674 target=_blank>Originally posted</a> by capn_hylinur
I was also told that you only need one gfci on one line even if you have have a dozen receptacles on the same line???
That is correct, as long as the GFI/GFCI is the first one in the circuit.
 
<a href=showthread.php?s=&postid=14068849#post14068849 target=_blank>Originally posted</a> by mcrist
That is correct, as long as the GFI/GFCI is the first one in the circuit.

thanks
I guess that would explain why he chose to add the gfi trip switch at the box rather then gfi's in the individual receptacles??
 
Hey Scott, The only thing with that installation is that when it trips everything is cut off from power not just the faulty appliance.
 